What is the minimum standard size overcurrent protective device required for a 120/208-volt, 3-phase feeder supplying a continuous load of 37.5 kVA?

Enhance your skills in code calculations. Test your knowledge with multiple choice questions, each with thorough explanations. Prepare effectively for your exam with practice questions and tips for passing, ensuring you're ready for success!

Multiple Choice

What is the minimum standard size overcurrent protective device required for a 120/208-volt, 3-phase feeder supplying a continuous load of 37.5 kVA?

Explanation:
In electrical installations, it's crucial to determine the appropriate size of overcurrent protective devices to ensure safety and compliance with national electrical codes. For a continuous load, you need to apply certain rules regarding sizing. First, calculate the load in amperes using the formula: \[ \text{Amperes} = \frac{\text{kVA} \times 1000}{\sqrt{3} \times \text{Volts}} \] For a 120/208-volt, 3-phase feeder with a continuous load of 37.5 kVA, this is calculated as follows: \[ \text{Amperes} = \frac{37.5 \, \text{kVA} \times 1000}{\sqrt{3} \times 208 \, \text{V}} \approx 104.1 \, A \] Since this load is continuous, the National Electrical Code (NEC) requires that overcurrent devices must be sized to handle continuous loads at 125% of their maximum rating. Therefore, the appropriate size calculation is: \[ \text{Minimum Overcurrent Device Size} = 104.1 \, A \times 1.25 \approx 130

In electrical installations, it's crucial to determine the appropriate size of overcurrent protective devices to ensure safety and compliance with national electrical codes. For a continuous load, you need to apply certain rules regarding sizing.

First, calculate the load in amperes using the formula:

[

\text{Amperes} = \frac{\text{kVA} \times 1000}{\sqrt{3} \times \text{Volts}}

]

For a 120/208-volt, 3-phase feeder with a continuous load of 37.5 kVA, this is calculated as follows:

[

\text{Amperes} = \frac{37.5 , \text{kVA} \times 1000}{\sqrt{3} \times 208 , \text{V}} \approx 104.1 , A

]

Since this load is continuous, the National Electrical Code (NEC) requires that overcurrent devices must be sized to handle continuous loads at 125% of their maximum rating. Therefore, the appropriate size calculation is:

[

\text{Minimum Overcurrent Device Size} = 104.1 , A \times 1.25 \approx 130